Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




View Full Version : Return registers


ralphe
10-18-02, 07:26 AM
I have a heat pump forced air system (in Connecticut) with resistive electric backup. The system appears to work as well as can be expected in this climate. There are several return registers. Some of these are paired. That is, there is one return duct that leads to two wall registers, one near the floor and one near the ceiling. Each register can be set to be opend or closed. My question is: which register should be open- does that change with the season (heating or cooling)?
thanks....ralph


resercon
10-18-02, 08:29 AM
Open the low return and close the high return in the winter because you want the coolest air in the room brought to the system to be heated and the warmest air to stay in the room.

The reverse is true in cooling. Open the high return and close the low return in the summer because you want the warmest air in the room to be brought into the system to be cooled and the coolest air in the room to stay.

ralphe
10-18-02, 09:29 AM
Many thanks....ralph