Quote:
Originally Posted by swallman View Post
Regarding the PVC, I wouldn't need to run that from the panel clear to the shed, would I ? Could I just run some 12-2 from the panel to a junction box where I convert to PVC ? ?!
You can run romex inside the house and then convert to the PVC when passing to the outside. I believe you will need 12-3. One thing about running a line to an out building, you can only run a single circuit. If you think you will need more then one circuit you will need to place a sub-panel in the outbuilding.


Quote:
Originally Posted by swallman View Post
Can I run Romex inside the PVC ?!
No, you can not run any type of cable inside of PVC or conduit. You must use individual conducters.