Thanks for the tips however Im still at a loss. I have taken the circ wires off the aquastat and placed them on the switching relay, as well as the thermostat wires. Now when I jump the TT switches on the aquastat Im not getting anything. So I agree the problem lies between my aquastat and burner.

the primary control is a honeywell r7184u when I test the leads going in I cant seam to get L1 power however I am getting 120 v at the Limit wire, and theres a note on top of the control that says that the Limit is tied in series with a line voltage thermostat ???