I have a Nordyne GR4GA gas package unit. When it starts up the inducer fan does not start up and the status light blinks twice.
Haven't had much experience with gas packs and none with Nordyne but two flashes usually means stuck-closed pressure switch. The control module first checks for a open switch before turning on the inducer. If the switch is already closed (activated) the control will not start the inducer and therefore not initiate ignition. Take a look at you switch. Suck and blow on the hose going to is and see if you hear a faint click. Check it with an ohm meter (with power off) while you do this to see if it opens and closes. If not replace the switch.