The clearance rule states that the panel must be located within a 30" space; it doesn't have to centered, it can be up to one edge of the 30". The clearance out from the panel must be 36". Basically, you need to be able to slide a refrigerator box up to the panel face without hitting any obstructions.

Based on the amount of work and expense required to relocate a panel, you might want to investigate reconfiguring the A/C duct instead.