Quote:
Originally Posted by thundercleese View Post
HUM2 goes through a 24 volt electronic relay and then to the humidifier.
Relay? is it this one below?


If you do have this, this is not needed since the IAQ takes care of turning on and off the unit as needed.

Quote:
What I noticed is when I cut power to the furnace and disconnected the wires from the humidifier to inspect the water still ran through the humidifier, could that point to a bad solenoid in the humidifier, or would that stay open even if power is disconnected?
sounds like the valve is stuck open. There is a spring inside of this, and a plungger. it will close when the power is off.

But go ahead and take it apart to clean it.