Quote:
Originally Posted by Jay11J This is not a furnace, it is an air handler for heat pump w/ electric heat back up. There is no hook up on here for the humidifier. You are kinda stuck with the sail switch, but there is another way we can wire it. you can wire it from G wire at the air handler to the humidistat. Humidistat to humidifier.. humidifier back to the air handler's C. |
I realized when I started more research on this model that it was referred to as an air handler. Furnace is just my generic term for it all since I don't know much about it.
So if I wire it that way, it'll give me my 24v from the G wire? Would I just get a new spade connector and put both wires into the same connector and back onto the G post? When would this tell the humifier to turn on, whenever the heat is on?
I have everything installed so far except the sail switch. So this would still be possible without any patching work.
Thanks for your help. I've read a lot of posts on here and you always seem to provide very good advice. Thanks!